\$\begingroup\$

I have a configuration where a medium-voltage switch connects directly to a transformer via a cable. There is no bus at the transformer side in the actual installation, as the cable terminates directly at the MV terminals of the transformer. However, ETAP automatically inserts a bus between the cable and the transformer. How should I configure this in ETAP to accurately reflect the real installation?

enter image description here

\$\endgroup\$
1
  • \$\begingroup\$ Try drawing a wire between XFMR and Cable28 if that does not work you will have to look at the parts in their library form and see how their pins are defined \$\endgroup\$ Commented Jun 15 at 0:32